How to generate an (re-) synchronized pulse train

Hello,
using a PCI-6601
I want to generate an endless pulse train of (e.g. 80Hz, high==low) synchronized to an external clock (ca.1Hz, ca 5ms pulse width).
The output should _re_synchronize with the clock if there is a clock signal but if one clock-pulse is missing it should continue hoping for the next.
It should look like this:
Perfect:
A1) tt________________tt________________tt_________...
A2) ooo___ooo___ooo___ooo___ooo___ooo___ooo___ooo__...
    0__1__2__3__4__5__6__7__8__9__0__1__2__3__4__5_...
Output is too fast:
B1) tt_________________TT________________tt________...
B2) ooo___ooo___ooo___oxxx___xxx___xxx___xxx___xxx_...
    0__1__2__3__4__5__6__7__8__9__0__1__2__3__4__5_...
Output is too slow:
C1) tt_______________PP________________tt__________...
C2) ooo___ooo___ooo__xxx___xxx___xxx___xxx___xxx___...
    0__1__2__3__4__5__6__7__8__9__0__1__2__3__4__5_...
Clock is missing:
D1) tt________________._________________tt__________...
D2) ooo___ooo___ooo___xxx___xxx___xxx___xxx____xxx__...
    0__1__2__3__4__5__6__7__8__9__0__1__2__3__4__5__...
The external clock is assumed to be "the truth", so the pulse width for the 80Hz output is recomputed from time to time
by measuring the clock and then setting then output pulse width.
Until now I used register programming but this is not a must.
The examples I've found either generate finite pulse trains or the sync only once.
Is there a way to do what I want without software interaction?
Thanks in advance
Toni Schilling

I have a possible idea for you, but my experience is with LabVIEW so I can't offer any help with register programming, interrupt callbacks, etc.  Also, the continuous syncing will have to be a software function that continuously performs cycles of measure/adjust, measure/adjust, measure/adjust...   I know of no way to set up the hardware to do this autonomously.
The approach I would take is to add another counter task and a little extra wiring.  The other task will be for "Two Edge Separation", and you want to measure from the active (lead) edge of the master clock to the passive (trail) edge of your sync'ed pulse train.  There's a reason NOT to measure to the active (lead) edge of your pulse train and it's because counters can only measure finite times of at least 2 timebase cycles.  Whereas you would *like* to have an actual two-edge separation time of 0 between the lead edges.  That just seems like the kind of detail that's gonna burn you sooner or later.
Let's just suppose the master clock is nominally about 1 Hz and your pulse train is nominally 100 Hz and 50% duty cycle so I can talk through details with some specifics.  Whenever the two lead edges are truly sync'ed, you'll measure a 0.005 sec two edge separation time from the master clock to your pulse train's trail edge.  If you measure slightly *less* than that, your pulse train is going just a little too fast and needs its freq slightly reduced.  If you measure slightly more, then your pulse train is too slow and needs its freq slightly increased.
It is probably quite likely that you *cannot* expect to maintain perfect sync *without* constant monitoring and adjustment.  Fundamentally, you can only produce pulses with high and low times that are an integer multiple of the 6601's timebase of 20 MHz.  That card's oscillator won't be perfect, nor will it be utterly constant over temperature variations, etc.   So its idea of a perfect 100 Hz pulse train will in fact be very very close but not *actually* perfect.
And your ability to adjust the frequency away from a nominal 100 Hz will only be possible in discrete steps.
A 100 Hz pulse train takes 200000 cycles of the 20 MHz clock.  If you adjust your square wave to take 199998 or 200002 cycles, you can produce a nominal freq of 100.001 or 99.999 Hz.  Those are the smallest increments away from 100.00000000 that are possible with a 50% duty cycle. 
Statistically, it's very unlikely that the frequency needed to perfectly match the external master clock is even *possible* to produce exactly.  I think you need to *expect* an imperfect sync with continual subtle adjustments to your pulse train.  If you watched the signals on a scope while triggering from the master clock, I think you should expect to see your pulse train oscillating back and forth by some small amount, perhaps in the microsecond realm.
Summary (for 1 Hz master clock, 100 Hz user pulse train at 50% duty cycle):
Measure two-edge separation from lead edge of master clock to trail edge of user pulse train.  Use units of "Ticks" with 20 MHz timebase.  Nominal expected value when sync'ed is (1/2)*(20 MHz / current user freq) = 100000.
Subtract measured ticks from nominal to produce your "error signal". 
Use current error signal its recent history in a control algorithm to determine the amount of adjustment to make to your pulse train.  Hint: it will probably NOT be correct to directly change the user pulse width by an amount equal to the error signal.  I suspect that you'll want to pay closest scrutiny to the derivative of the error signal.  Note also that the correct AMOUNT of adjustment will depend on the RATE at which you run your measurement / adjust loop.
Change user pulse specs on-the-fly.
Return to step 1.
Caution: Let's suppose your software measurement / adjust loop runs at a nominal 10 Hz.  From the time you make an adjustment until the next time you do a measurement, your user pulse train will have generated almost 10 cycles with the recently-adjusted specs.  If you weren't careful to make your previous adjustment subtle enough, you'll find that you now have a *larger* error of the opposite sign, and you are well on your way to instability.
   You need to do an adjustment that lets you expect your *next* measurement to have an error close to 0.
-Kevin P.

Similar Messages

  • HOW TO GENERATE FINITE AND CONTINUOUS PULSE TRAIN WITH USB6216 AT THE SAME TIME?

    Hello.
    I am using a USB6216 DAQ and need to generate a 20 kHz signal using the
    ct0 output and at the same time I need to generate a finite number of
    pulses, say 9, on a software trigger using the second counter output
    ct1.
    Currently, I have two VIs that can do this separately, but when I want
    to integrate these into one single VI y get an error in the finite
    pulse train for ct1 that indicates that the requested task is already
    reserved. I am thinking this has to do with the fact that maybe both
    types of task use the same timebase but I have not found the way to
    solve this problem.
    Any help would be very much appreciated.
    Thank you.
    Sincerely
    JSL

    Hello.
    If anybody is interested, the problem is solved.
    There is no resource confilct if I generate the 20 kHz continuous pulse
    signal using the frequency out terminal, and this way I can use both of
    my counters as I please with no problems.
    It's kind of fun to answer one's own questions...
    Sincerely
    JSL

  • On E series Card with 2 counters I want to generate a fixed length pulse train and want to continuously monitor it.

    On E series Card with 2 counters I want to generate a fixed length pulse train and want to continuously monitor it.

    Depending on the software you are using, there are many shipping examples and example programs on the web that illustrate generating a finite pulse train. The E series boards have the DAQ-STC counter/timer chip, and so make sure you search for DAQ-STC examples. I have included links to a LabVIEW example and Measurment Studio Example in Visual Basic.
    Generate finite pulse train in LabVIEW.
    http://eagle.ni.com/stage/we/niepd_web_display.DISPLAY_EPD4?p_guid=B45EACE3DA2156A4E034080020E74861&p_node=DZ52328&p_submitted=N&p_rank=&p_answer=&p_source=Internal
    Generate finite pulse train in Visual Basic with Measurement Studio
    http://eagle.ni.com/stage/we/niepd_web_display.DISPLAY_EPD4?p_guid=B45EACE3D96156A4E034080020E74861&p_node=DZ52328&p_submitted=N&p_rank=&p_answe
    r=&p_source=Internal

  • How to generate a delayed retriggerable pulse using only one counter with PXI 6070E card

    Hi
    I have a problem in generating a retriggerable delayed pulse with a single counter(triggered through a signal at gate) using PXI 6070E card. VI was developed in NI LabVIEW traditional DAQ Ver.7.1. I have used the "delayed pulse generator config" VI and a "Start counter" & "Stop counter" VIs for the purpose. But there is no output seen at the out terminal of counter. So I introduced a "wait" VI and set it to 1 sec. Now the pulse output appears but some pulses are missing mometarily after every 1 sec interval. (any solution for this)
    I have gone through a few similar requests in the forum but they suggest either to use two counters or to generate a finite pulse train which does'nt fit my application. Moreover PXI 6070E has only 2 counter timers. I am already using one counter to measure the frequency of a pulse train(signal 1). The application requires to generate a delayed retriggerable pulse for every pulse in signal 1. So I have only one counter left.
    Can I measure the frequency of signal 1 by analog means.? so that I can use two counters for pulse generation. (Signal 1 is a TTL signal).
    Request some help.
    Thanks in Advance
    Regards

    A finite pulse train (N_Pulses >= 2) does require the use of 2 counters on most of our older hardware including your 6070E.  If you're just talking about generating a single retriggerable pulse, you would only need one counter.
    Here's an example in Traditional DAQ that shows you how to set a retriggerable pulse generation (it also allows you to adjust the characteristics of the pulse on-the-fly).
    If you're writing a new program, you might consider switching to DAQmx as it supports NI's latest hardware and recent OSes should you ever need to upgrade.  Traditional NI DAQ is no longer in active development.  Here's an example of how to implement a retriggerable pulse generation in DAQmx.  You should take note that you can't use the two drivers to simultaneously talk to the same piece of hardware, although you should be able to go back and forth by resetting the Traditional DAQ driver before switching to DAQmx.
    Best Regards,
    John Passiak

  • How do I output a finite pulse train through multiple counters?

    Hello,
    I have used LabView examples to create a VI to use with my TIO 6602 that generates a finite pulse train with varying duty cycle, frequency, number of pulse, and initial delay.  I can also have it output the pulses through multiple counter channels, but all the channels have the same delay, and are output at the same time.  I need each channel to have a specific delay from the first one.
    In my VI, I use DAQmx to create a retriggerable finite pulse train by gating a counter with another counter.  I have all the neccessary controls over the pulse train, but I can not seem to find an easy way to just copy this waveform and output delayed versions of it to other channels.  The delay is very important because these signals will be used to drive ultrasound transducers in a linear array, and for the waveforms to focus at one point, the signal driving the transducers with a shorter distance from the focal point need a larger delay, so that the same waveform arrives from each transducer at the same time.
    Any help with how I might do this would be much appreciated.
    Thanks!

    Hey Sneaky,
    Here's a screenshot of the code I put together on how to use multiple counters.  Also, take a look here for more information on how to sync multiple counters. 
    Message Edited by Knights Who Say NI on 02-02-2009 10:36 AM
    Message Edited by Knights Who Say NI on 02-02-2009 10:36 AM
    Message Edited by Knights Who Say NI on 02-02-2009 10:38 AM
    -John Sullivan
    Analog Engineer
    Attachments:
    4xcount.jpg ‏67 KB

  • How do you set amplitude of pulse train?

    I have successfully downloaded and executed the sample program shown here:
    http://www.ni.com/white-paper/2991/en
    and see the pulse train generate in my oscilloscope.  When measuring the value of a pulse high, the oscilloscope says 5V. 
    How do I change it to 3?
    Looking at the DAQ Create Channel node I don't see any inputs for amplitude, only frequency and duty cycle.
    Where is the amplitude of 5volts being set and how can I change it to 3V?
    Solved!
    Go to Solution.

    Hi Nathand, and Ricky - 
    Do you guys think this website:
    https://decibel.ni.com/content/docs/DOC-3545
    Could help me? I noticed there is a minimum and maximum value passed in to the Analog Output function.  
    I could set the minimum = 0V and maximum = 3V.
    I will also look into the level shifter and transistor ideas.

  • How to change the frequency of pulse train on the fly using an array of values?

    Hi all!
    First I want to thank U for the great job you are doing for this forum.
    Iam still busy trying to control a stepper motor, by sending pulses from my E-series 6024 to a compumotor s6- stepper Driver. I've managed to get it working. I desperately need to control the motor using the values from an array. I believe we can use two approaches for that:
    1st - I can get an array of the "numbers of pulses". Each element must run for 10 milliseconds. Using that we can calculate the array of frequencies to send the number of pulses within 10 milliseconds for each specific element. Could we use the arrays of "number of pulses" and frequencies in a "finite pulse train " and up
    date with each element every 10 millisecond?
    2nd - Or Could we use of the frequency array in a "continuous pulse train vi" and update it every 10 milliseconds?
    Please note that I must use the values as they are.
    Can someone please built a good example for me? Your help will be appreciated.
    Regards
    Chris
    Attachments:
    number_of_steps.txt ‏17 KB
    frequency.txt ‏15 KB

    Tiano,
    I will try to better explain the paragraph on LabVIEW. The original paragraph reads ...
    "While in a loop for continuous pulse train generation, make two calls to Counter Set Attribute.vi to set the values for "pulse spec 1" (constant 14) and "pulse spec 2" (constant 15). Following these calls you would make a call to Counter Control.vi with the control code set to "switch cycle" (constant 7). The attached LabVIEW programs demonstrate this flow."
    You can make two calls to Counter Set Attribute or you can make a call to Set Pulse Specs which, if you open this VI, you will see that it is just making two calls to Counter Set Attribute. What you are doing with the Counter Set Attribute VIs is setting two registers called "pulse s
    pec 1" and "pulse spec 2". These two registers are used to configure the frequency and duty cycle of your output frequency.
    The example program which is attached to this Knowledge Base demonstrates how to change the frequency of a continuous generation on the fly. Why continuous? Because changing the frequency of a finite train would be easy. When the train completes it's finite generation you would just change the frequency and run a finite train again. You would not care about the time delay due to reconfiguration of the counter.
    If you would like to change the frequency of the pulse train using a knob, this functionality will have to be added in the while loop. The while loop will be continuously checking for the new value of the knob and using the knob value to set the pulse specs.
    LabVIEW is a language, and as with learning all new languages (spoken or programatic) there is a lot of learning to be accomplished. The great thing is that LabVIEW is much easier than mo
    st languages and the learning curve should be much smaller. Don't fret, you'll be an expert before you know it. Especially since you're tackling a challenging first project.
    Regards,
    Justin Britten

  • How do you create a finite pulse train using a FP-CTR-502?

    I have recently replaced my FP-PG-522 module with a FP-CTR-502 module, to achieve higher output frequencies (FP-PG-522 max output freq is 5kHz, wheras the FP-CTR-502 max output freq is 16 kHz).
    I need to be able to generate a finite pulse train. Has anybody created a finite pulse train using a FP-CTR-502 module before? I have started to look into it, but my ideas so far have been complicated (compared to doing it in a PG module).
    Any tips on this would be much appreciated.
    Christopher Farmer
    Certified LabVIEW Architect
    Certified TestStand Developer
    http://wiredinsoftware.com.au
    Solved!
    Go to Solution.

    I can answer this question myself!
    The answer is in the *OLD* version (July 2000) of the operator's manual for the FP-CTR-502. For some reason, this has been removed from the latest version (June 2003).
    See page 11 of this link for more information:
    http://www.ni.com/pdf/manuals/322660a.pdf
    Christopher Farmer
    Certified LabVIEW Architect
    Certified TestStand Developer
    http://wiredinsoftware.com.au

  • How do program 3 independent finite pulse train generators from 3 counter pairs

    I need to drive a 3-axis piezo leadscrew friction type motor by finite train of pulses from a PCI-6602.How do I specify the counter pairs in my code with out any one counter conflicting with the others?
    Bernardino Jerez Buenaobra
    Senior Test and Systems Development Engineer
    Test and Systems Development Group
    Integrated Microelectronics Inc.- Philippines
    Telephone:+632772-4941-43
    Fax/Data: +632772-4944
    URL: http://www.imiphil.com/our_location.html
    email: [email protected]

    This scheme (and the examples) works fine when you want finite generation done in sequence, but seems not to work with when they are done independently and in synchronously run in parallel fashion.
    Berns B.
    Bernardino Jerez Buenaobra
    Senior Test and Systems Development Engineer
    Test and Systems Development Group
    Integrated Microelectronics Inc.- Philippines
    Telephone:+632772-4941-43
    Fax/Data: +632772-4944
    URL: http://www.imiphil.com/our_location.html
    email: [email protected]
    Attachments:
    Mutliaxis_test_drive_version_0.vi ‏85 KB
    NF8096Exercise.vi ‏206 KB

  • How to generate a single output pulse on 64 different digital out lines (PCI-6513) each with a different start time relative to an event in a main program loop.

    Long question.
    I am running a main program loop of 60 msec. At one point in the loop I create a 64 element array of delay times. At that point I need to begin outputting a predefined single pulse to each of the 64 lines on my PCI-6513. Each line outputs the pulse with a starting delay set by the "delay time" in the array.
    Each delay time is such that the pulses will be done before the next loop commands another one.
    Thank You
    Roger

    Hi,
    You have multiple ways of doing this, since there is no timing engine on the 6513 your code is going to control the output of the card, which is what we called “software timed”.  If you take a look at the example called: “Write Dig Chan.vi”, you can individually control each line.
    So to change the state of the line; since you have an array of delays time you can aid yourself with “stacked sequence structure” where in each frame you control the time it takes to go to the next frame and the data been written to the card.
    Another option is using a state machine where each state write the data you want and you can also control the time between states. For further references take a look at this article Application Design Patterns: State Machines.
    I hope it helps
    Jaime Hoffiz
    National Instruments
    Product Expert
    Digital Multimeters and LCR Meters

  • Generate pulse train

    hello,
    i have a question:
    how to generate a 7 Hz pulse train with a daq dt304???
    Thank you very much.

    Found what I was looking for. The resulting page upon posting this question had a link to the LabVIEW palette upgrade for new counter VI's.

  • How to continuously generate a pulse train with variable frequency

    Dear all,
    I am trying to use NI-USB 6259(BNC) to send Pulse signals to conduct position control of a servo motor with labview. The position control of servo motor follows these rules:
    The number of the pulse train determines how many degrees the motor rotate ;( e.g. the angular position of motor)
    The frequency of pulses determines how fast the motor rotate; (e.g. the speed of motor rotating)
    The digital determines the direction of rotation of motor (e.g. clockwise or counterclockwise)
    My question comes when I need to continuously generate a finite plus train signal in a period of time. Below is a sample:
    Time(s)
    Number of pulses
    Direction of rotation
    (1 is clockwise, 0 is counterclockwise)
    Frequency
    0-1
    923
    1
    923hz
    1-2
    3540
    0
    3540hz
    2-3
    1751
    1
    1751hz
    3-4
    2663
    0
    2663hz
    4-5
    353
    0
    353hz
    5-6
    1017
    1
    1017hz
    6-7
    3436
    1
    3436hz
    7-8
    302
    0
    302hz
    8-9
    1513
    1
    1513hz
    9-10
    570
    1
    570hz
    Here is the explanation of this table, the motor keeps rotating in clockwise direction during 0~1s. When the time reaches 1s, the motor just complete the rotation of 923 pulse signals. And then the motor starts to rotate in counterclockwise direction during 1s~2s. When the time reaches 2s, the motor just complete the rotation of 3540 pulse signals. So we can see that the rotating speed of motor in 0~1s is different from the speed in 1s~2s. Namely, the frequency of pulse signal in 0~1s is different from the frequency in 1s~2s.
    I have already use the counter output of DAQmx, it just can generate pulse signal with certain numbers and certain frequency in one time. The attachment is the vi which can generate a finite digital pulse train from a counter output channel and the frequency, duty cycle, Initial delay, and Idle state are all configurable.
    How can I continuously generate  a series of pulse train with varying numbers and frequencies during a certain period of time.
    Thank you very much for your help!
    Solved!
    Go to Solution.
    Attachments:
    Counter - Finite Output.vi ‏57 KB
    Finite output.png ‏13 KB

    Hi aacuna,
    Thank you for your reply!
    I already checked that  article.  The frequency in that Vi can change dynamically, but the method of adjusting the frequency is ‘manual’ .Below is the front panel of that Vi. When the Vi is running we can change the frequency by press the button.   
    Time(s)
    Frequency
    0-1
    923hz
    1-2
    3540hz
    2-3
    1751hz
    3-4
    2663hz
    4-5
    353hz
    5-6
    1017hz
    6-7
    3436hz
    7-8
    302hz
    8-9
    1513hz
    9-10
    570hz
    Thank you!

  • How to generate sequence of pulse trains with DAQmx?

    I need to generate a sequence of pulse trains with DAQmx (the card I have is a PXI-6229 card). As an example:
    - 10'000 pulses at 20kHz every 5 seconds with an initial offset of 2 seconds (let's say 10 pulse trains in total).
    If I use the CreateVirtualChannel.vi in "CO pulse ticks" mode, I can only specificy offset, high ticks and low ticks, but not that the sequence of pulses should be repeated after some time. 
    Now I thought that I could solve this problem if it were possible to multiply two counter outputs: the first counter would generate the pulses (continuously) whereas the second one would switch between low and high on a slower timescale in order to gate the first counter, thereby providing an initial offset and the "off" phases between the pulse trains.
    Is it somehow possible to multiply two outputs with DAQmx and the card I have? Or is there another solution to the problem?
    Thanks a lot in advance for any hints!

    Hi dlanger,
    what you want to do requires a little bit more work. 
    First look at the example "Gen Dig Pulse Train-Continuous.vi" from the LV example finder.
    This example generates a continuous* pulse train. As you see, you need a sample clock VI for setting the sample mode. 
    * NOTE: Generating a finite pulse train with a M-series card requires 2 counter.
    With a pause trigger (DAQmx trigger property node) you can gate the output of that counter.
    Now you have to generate a gate-signal with the the 2nd counter. That means, only if  Ctr1-out is high Ctr0-out outputs the 20 kHz-signal. 
    Maybe you have to adjust the times in my example a bit. 
    Unfortunately there is just one "small" problem: "let's say 10 pulse trains in total" 
    This is not possible, because a 3rd counter would be necessary (*). 
    As a workaround you can modify the while-loop that both tasks are cleared after 50s. This is not brilliant, but should work fine for you. 
    A more sophisticated way is to perform a correlated DIO. So you can generate custom pattern for multiple outputs. 
    A good example can you find here: 
    Retrigger and Repeat Finite Digital Pulse Train in LabVIEW
    http://decibel.ni.com/content/docs/DOC-8473 
    or here:  
    Generating More Than 2 Pulse Trains Using CompactDAQ
    http://decibel.ni.com/content/docs/DOC-2167 
    Hope this helps.
    With best wishes,
    Ralf N. 
    Attachments:
    Gen Gated Dig Pulse Train-Continuous.vi ‏38 KB

  • How to get delayed pulse train

    hello,
    i am using Labview 7 and a PCI 6014 interface card. i want to generate delayed pulse train. for this purpose i am generating a analog waveform using 'function generator.vi'. i supply this waveform to a counter and to generate delay i am using 'finite pulse train(daq-stc).vi'. when i set trigger mode to 'no trigger', the VI works fine. But if i supply generated waveform to the counter gate(i.e. setting trigger mode to external), i see for sometime pulses missing are missing. I have also tried several other VI's(like 'delayed pulse easy.vi' and 'cont pulse train easy.vi'), but facing same problem. Can you please tell me how can i solve this problem.
    regards,
    Abhijeet

    hello Alan,
    Ok! here i explain my code. My requirement is to supply contineous 5V pulses at around 10Hz to a camera. After some time of the rising edge of pulse to the camera, i want to trigger Laser-1 and after some time of rising edge of the pulse to the Laser-1, i want to trigger Laser-2. In PCI 6014 there are only two counters which i am using for two Lasers(for delay generation). For Pulse train generation i am using 'function generator.vi'which is basically a waveform generator, but to get pulse train i set offset equal to amplitude. I supply this pulse train to two counters. To generate delay from the counters i am using 'Delayed pulse easy(9513).vi' which i have put into while loop. To see the output i am using 2-channel oscilloscope vi where i see some pulses missing. Also I obsereved pulses missing when i supply the output to the Lasers(Lasers stops firing for moment).
    I am attaching a timing diagram which is explains my application and a labview code where i have combined three VIs (one 'function generator.vi' and two 'delayed pulse easy(9513).vi').
    Thank you,
    Abhijeet
    Attachments:
    camera+laser1+laser2.vi ‏188 KB

  • Finite pulse train with different frequency

    Hello,
    I'm trying to modify the labview example "generate finite pulse train" to generate a finite pluse train with different frequencies. Each freq will run 400 pulses. The freqs are stored in an array, which is being fed into a for loop. Thus ramp up the freq each iteration. However the program only generate 400 pluse at first given freq. I'm fairly new to daqmx and not sure what is wrong. Anyone have some idea how to fix it?  
    Attachments:
    pulse train finite mod.vi ‏38 KB

    The best "fix" will depend a bit on the needs of your app.
    Is it ok to have a fraction of a second without any pulses each time you change frequencies?  If so, then there's a pretty simple solution:
    1. Outside the loop you'd create a DAQmx virtual channel and configure for Finite Sampling (# samples = 400) using DAQmx Timing.vi.  
    2. Inside the loop you'd chain together a DAQmx Channel property node where you set the pulse frequency property, then perform a DAQmx Start, a DAQmx "Wait for Task Complete", and a DAQmx Stop.
    3. So for each freq in your array, you'll program the counter for that frequency, start the generation of pulsetrains, and then stop the task after 400 pulses have been generated.
    If you must change frequency on-the-fly, producing *exactly* 400 pulses at each freq setpoint will be tricky, and maybe even impossible to do reliably.  Some techniques will get you closer than others though, so post back if you need to do this.
    -Kevin P.