Does anybody knows the typical time that a FPGA card, like PXI 7831, take to generate a TTL signal on one of its digital lines?
To be much clear, imagine you read a digital line on your PXI 7831 as fast as possible (40 MHz...?) and then generate a TTL high signal when you see a rising edge on digital input...What you be the delay between the two signals?

The delay between reading an edge on the input line and updating an ouput line will depend on the exact requirements of your application and the implementation of the code based on that. There are two main ways to implement this type of application.
You can continuously read the input line and then in your LabVIEW code check for a change of state and if one is detected, update the output line. The delay between reading the input and updating the output will be 2 or 3 clock cycles of the FPGA (50-75 ns at 40 MHz). However since this code would be running in a loop, the loop overhead is added to the possible delay as the change on the input line may occur at any time. So the maximum delay may be around 6 to 8 clock cycles.
The second method to implement t
his code is to use the Wait for Edge function in LabVIEW FPGA. This function will wait for an edge on a digital input line and continue when an edge is detected. The delay will be 2 to 3 clock cycles, however the application will not be cycling through the loop if no edge is detected.
Depending on the complexities of your diagram you may be able to compile your code for an 80 MHz FPGA clock rate in which case the delays would be cut in half.
Christian L
NI Consulting Services
Christian Loew, CLA
Principal Systems Engineer, National Instruments
Please tip your answer providers with kudos.
Any attached Code is provided As Is. It has not been tested or validated as a product, for use in a deployed application or system,
or for use in hazardous environments. You assume all risks for use of the Code and use of the Code is subject
to the Sample Code License Terms which can be found at: http://ni.com/samplecodelicense

Similar Messages

  • Controlling fpga digital output node from realtime boolean

    I have a system where I want to turn on / off a digital output running on the FPGA.    
    Once I set the boolean on my realtime side (which turns on the FPGA output), I see the output turn on the CRIO, but it flickers on and off.   (not latching?).   I just want the FPGA to stay on as long as the output is turned on, on the realtime side.  I cant change the mechanical action of the switch due to limitations on FPGA / RT according to labview ( I get an error at compile)
    Any suggestions on how to correct this?
    Solved!
    Go to Solution.

    I have simplified my program to something very basic to replicate the problem. 
    The digital output D0 switches on and off everytime the realtime loop cycles through. 
    If I run just the FPGA seperate and turn on the digital output control D0 it stays on solid. (until I turn it off again)
    What am I doing wrong?
    Attachments:
    FPGA_RT_TEST.zip ‏144 KB

  • Digital Output With Timer (Simulation)

    Hello everyone, I just learned how to make LabVIEW program a week ago. I try to make a simulation of Digital Output by LabVIEW (my attachment). In this simulation I have a slider as an input (0-10 V), two numeric control (upper limit and bottom limit), a waveform chart that plot those 3 value, and two boolean LED (P0.0 and P0.1) as an indicator. In this simulation you can fill any number (between 0-10) in the numeric control as a limit for your slider input. If the input from a slider exceed those upper and bottom limit then the boolean LED will turn on, P0.0 if exceed upper limit and P0.1 if exceed bottom limit. The problem is I don't know how to make timer for those boolean LED. As example:
    1) Make an input from slider,
    2) If input (1) exceed the upper limit,P0.0 will turn on for 5 second,then turn of for 10 second,
    3) If in that 10 second you change the input back to normal (between upper and bottom limit) then P0.0 will stay turn of until the input from slider exceed the upper limit again,
    4)If in that 10 second you didn't change the input (stay exceed the upper limit) then P0.0 will repeat the process (2) until you the input from slider back to normal.
    (Same process for input that exceed the bottom limit).
    Can you help me to make this timer? Thank You (I'm sorry I made a double post):newbie
    Regards
    Juventom
    Attachments:
    Digital Output With Timer.vi ‏16 KB

    Hello Juventom,
    As I understand it you want to be continuously checking the value of the sliding bar and comparing that to the upper and lower limit controls whilest also chaning the LED booleans to true for 5 seconds then false for 10 seconds if the sliding bar value is outside of the limits.
    To do this you would probably be best using a parallel loop design, where you have 3 while loops in place of the one you have currently. Each one of these while loops would be responsible for a part of your program (e.g. the top one would display your values on the graph and the second one who check the sliding bar value against the upper limit and then turn on the LED, etc)
    I've found this tutorial about multiple loop programs and I think you should look at the section entitled "Parallel Execution"
    http://zone.ni.com/devzone/cda/tut/p/id/3749
    This way you can use normal delay VIs but when they run they only pause that loop rather than the whole program.
    Please let me know how you get on with this, and ask me if you need further help.
    James W
    Controls Systems Engineer
    STFC

  • Setting time critical digital output based on axis position (PCI-7358)

    HI,
    I need to set a time critical digital output based on encoder position (this will switch fast acting valves). I was planning to try the general purpose DIO but I can't find any examples, I have been through the manuals, searched the site etc. Where can I find help with this, all the examples only seem to deal with digital input triggering or RTSI? I'm thinking of an onboard program that just monitors encoder positions and sets digital outputs.
    Some time back I seem to remember reading that general purpose DIO should not be used for time critical operations, is that correct? And if so what are the other options - RTSI going to another DIO board? The DIO really needs to be deterministic, is RTSI the only option?
    Any advice appreciated / Martin
    Certified LabVIEW Architect

    Even with an onboard program you will always get a delay of several milliseconds between your axis has crossed the position and until the digital outputs are set. If this is ok for you then you could choose this approach.
    For the case that you only want to toggle one digital line the Breakpoint feature should be the best solution as it toggles the breakpoint output almost immediately when the breakpoint positions are reached.
    If you need to change a whole pattern instead of only a single line then the approach you mentioned would be the best solution (RTSI and high-speed DIO like the 653x boards). Combine this approach with the breakpoint feature by routing the breakpoint output to RTSI and using this as a update clock signal for the DIO board.
    Best regards,
    Jochen Klier
    National Instruments Germany

  • How do I control a digital output on NI9144 FPGA with fpga code running on NI9082.

    Due to a recent change in our hardware configuration I need to locate my various I/O modules in various locations around the facility. I am attempting to use an etherCAT setup consisting of an NI9082 and multiple NI9144 (for now only one NI9144). I need both devices to run code in the respective FPGA and make the results available to the other devices and for user interface software. My question is is it possible for the two FPGA code segments to communicate directly with each other without going through the RT or computer interfaces. I need to fire a digital output bit on the NI9144 based on logic running on the NI9082.
    Are there any good code examples around that someone can point me to?
    Thanks for the help.

    Hi, you can include trigger conditions (digital, or analog) on your FPGA VI and connect directly the I/O from module to module (analog with analog & digital with digital), however, if the chassis are meant to be at different locations the cable used to connect the ports is equals the length in between each device and that could degrade the signal if we are taking about a couple meters or kilometers. The most reasonable way to send/receive data from great distances is through ethernet using a regular communication protocol (such as TCP/IP, network streams, network shared variables...etc).
    Alejandro | Academic Program Engineer | National Instruments

  • Digital input and digital output at the same time

    Hi all
    I have a PCI-6503 board. I have done 2 task that run simultaneously: the first one is port0_16 output and the second one is port2 input.
    I get sometimes (not every times...this is strange...) error-200587 saying:
    'Requested operation could not be performed, because the specified digital lines are either reserved or the device is not present in NI-DAQmx.
    It is possible that these lines are reserved by another task, the device is being used through the Traditional NI-DAQ interface, or the device is being reset. You might also get the error if the specified resource is currently in use by LabVIEW network variables bound to the DAQ Channel, or if the DAQ Channel is being used in any OPC Client software.
    If you are using these lines with another task, wait for the task to complete.  If you are using the device through the Traditional NI-DAQ interface, and you want to use it with NI-DAQmx, reset (initialize) the device using the Traditional NI-DAQ interface. If you are resetting the device, wait for the reset to finish.'
    In the attached VI i have recreated the basic structure of my real VI (the error is present even here of course...).
    How can i do?
    I want to have both digital input and digital output with the same PCI-6503 every single cycle... Is it possible?
    Please help me!!!
    Kind regards.
    I love the smell of napalm in the morning
    Attachments:
    DIO simultaneously error.vi ‏31 KB

    Hello Maverick,
    Did you have any luck with the example Raven sent you?
    In Raven's example, it properly passes the DAQmx task from one SubVI to another to avoid having to open the task again. These errors are likely to occur when you have multiple DAQmx calls in a VI that call the same task again without clearing the previously opened task. If at any given time you try to open a task that already is being used, you might receive an error "resource is reserved"... similar to your original example.
    If you are interested, here is an awesome link that gives a detailed explanation of the LabVIEW dataflow paradigm
    Learn 10 Functions in NI-DAQmx and Handle 80 Percent of Your Data Acquisition Applications
    Thanks and good luck!
    Jordan Randall
    National Instruments Italy

  • Button timer digital output

    Hi folks,
    Want to control digital output USB6215 with button. The active time presetable from control, like 5.2 seconds
    Hopefully simple solution
    -Stefan

    srydstrom wrote:
    Hi folks,
    Want to control digital output USB6215 with button. The active time presetable from control, like 5.2 seconds
    Hopefully simple solution
    -Stefan
    it is a simple solution..have you looked at the NI shipped examples? Goto Help>Find Examples...>Hardware Input and Output>Daqmx>, if your button is external hardware...you need "Analog Input or Digital Input" to acquire the signal..if not, then software controlled...this all needs to be sent to >Digital Output.
    note: the Requirements box will indicate what NI devices you can run with these examples...

  • Write digital output on wireless node

    hello
    i have wsn kit with 9791 gateway, i need to program node 3202 to write a digital output, i want to know how can i do this in labview ?
    do i have to write program ? what library in labview should i chose ? is it using FPGA module in labview ? i really spent alot of time searching for this answer and i am new in labview program
    thank you 

    Hi,
    In order to use the WSN-3202 with Gateway-9791, you have to install LabVIEW and NI-WSN driver.
    You can find the software version support for your WSN at http://zone.ni.com/devzone/cda/tut/p/id/12734#toc0.
    After you have install the software, you can configure your WSN using Measurement and Automation Explorer (MAX) and add WSN node to the gateway, it might not looks exactly the same in the picture below because I am not using 9791 as the gateway.
    Next, you can open an empty project or your existing object and add your gateway into your project.
    After you add the gateway and your node into the project, you can access the DIO at WSN-3202 through the share variable node. You can just drag the DIO from the project explorer into your vi.
    Best Regards,
    KH
    Application Engineer

  • How to give delay in switch on digital output lines

    Hello All,
    I am working on PCI-6514 Digital IO card, I am writing a sequence to my application using DAQmax for  Digital input and output lines
    I want to switch on one output line0 and after a delay 5sec switch on line1 output and after a delay of 3sec switch on line2 output and sense input line 0 and line 1 .
    How can we know the status of output ie output is on or off.
    Since i am using the IO card for first time suggest me in this.

    Hi
    I am going to assume that you are using LabVIEW 7.1 for this application.  If you are trying to acquire data from an external device after outputting data to that device, the DAQmx tristate property node will give you this functionality.
    You will then need a DAQmx write.vi to output your digital data followed by a DAQmx channel property node. Select Digital Output>>Tristate on the property node and wire a true constant into it. After the property node, you can use a DAQmx read.vi to read the data coming into the digital lines. By using the tristate property node, you can avoid stopping the digital output task and starting an entirely new task.  I am attaching an example program that will demonstrate this.
    Regards,
    Hal L.
    Attachments:
    digital input and output.vi ‏39 KB

  • Create 4 digital output pulses base on input ttl signal

    Hi
        I am a beginner in Labview and would appreciate any advice on how to solve the following problem.
    I am creating a TTL pulse train, and would like to send that into Labview as input.  For every falling edge detected on the input signal, I'd like Labview to generate 4 digital output pulses.  For each output pulse, I'd like to be able to specify the delay, and duration.       The picture should illustrate it more clearly, with the numbers showing the intended order of magnitude.
    System:  NI PCI-6733 DAQ card, Labview 8.5
    My daq card has 2 24-bit timers, and 8 digital I/O but I don't know what the best approach is for creating between 4-8 output pulses of this precision..should it be handled in hardware, or in software?  And how would I go about it
    Thanks,
    -Sidney
    NI Hardware: PXI-7853R, PCI-5122, PCI-6733, PXI-1036, PCI-MIO-16E-4, PCI-6110
    Computer Hardware: Xeon Quad Core - 2.33 Ghz, 8 GB RAM
    Software: Labview 2009, Labview FPGA 2009, Vista 64-bit, MAX 4.6, DAQmx 9.0, NI-SCOPE 3.5
    Solved!
    Go to Solution.

     Hi Yann,
       Wow, thank you so much for this example!  I'm trying to take a look at it, but when I run it.. it responds with the following error message
    Error -200452 occurred at Property Node DAQmx Trigger (arg 1) in DAQmx Start Trigger (Digital Edge).vi:1->reprise-1.vi
    Possible reason(s):
    Measurements: Specified property is not supported by the device or is not applicable to the task.
    Property: Start.TrigType
    Task Name: _unnamedTask<49>
    This is strange too, because ive already used the Digital Edge Start trigger for a different application with this card.
    -Sidney
    NI Hardware: PXI-7853R, PCI-5122, PCI-6733, PXI-1036, PCI-MIO-16E-4, PCI-6110
    Computer Hardware: Xeon Quad Core - 2.33 Ghz, 8 GB RAM
    Software: Labview 2009, Labview FPGA 2009, Vista 64-bit, MAX 4.6, DAQmx 9.0, NI-SCOPE 3.5

  • Digital Output Stopped Working

    My new 1.66 Intel Core Duo Mini has been flawlessly passing digital audio to my receiver from VLC and EyeTV for close to a week. But I played a DVD for the first time today with Front Row and ran into a huge problem.
    While there was no trouble playing Dolby Digital from Front Row, now I can't get any sound through the digital output outside of Front Row. VLC is silent and EyeTV needs to manually change over to "system sound output" for anything to get through. And then it's in stereo, despite Dolby Digital showing up as the soundtrack in EyeTV.
    I combed this forum but couldn't find this specific problem. I saw someone recommended flashing the nvram as a possible solution to problems with the digital output but wanted to see if anyone had any other ideas.
    1.66 Intel Core Duo 1GB RAM   Mac OS X (10.4.6)  

    On a somewhat related issue: My Mac Mini 2007 won't output audio, via toslink mini adapter. It shows up in the Midi output as working and I see the red light from the cable. But when I put in a regular mini audio cable, and "move it around" in the headphone slot I get sound if it's just in the right place. Is this some sort of short in the headphone jack inside the Mini? Does this need to be replaced or is there an easier solution? Comments appreciated!

  • Digital Output problem once again (WIN XP, Audigy

    I searched the forums with no luck, actually I searched the whole internet with no luck - so far.
    My problems in a nutcase:
    - I can't find the button for Digital Output (the one which enables it, Windows XP's sound mixer used to have that option with some ?windows build?, but I can't find it since I installed creative drivers, it's just gone...).
    - If I find the digital output on-button with your help, is it even possible hear music with add-ons trough digital-optical cable or should I buy some mono-cable? :O
    To be specific:
    I have the Creative Audigy 4 Bulk, which of course supports SPDIF Digital output. I bought expesi've optical cable that I could finally use my hifi 5. speakers with movies trought computer. I have new 700 euro amplifier, and it supports everything, so the problem isn't with that one, anyways, let's get touch with the real problem.
    What ever drivers I'm using, I can't find the digital output section anywhere. Creative drivers has one SPDIF-button, but it affects nowhere. So, I can't even get the Digital Sound on, because windows mixer has no button for that with my windows xp, weird. I also tried to install windows vista, and there wasn't either any options, where I could put the digital output on.
    Which drivers and which add-ons should I install to get that Digital Output to work.
    If I manage to find the button for digital output from some drivers, can I also listen music while it's connected via optical-digital cable, or am I just able to hear sound from dolby digital movies? Is it even possible to get everything work with my optical cable (music/games and movies at the same time).

    . Your card doesn't have optical output, only "coaxial" digital. You will need a stereo (or camcorder) cable with one mini jack on one end and 2 (or 3) RCA connectors on the other. The white RCA will be the one you need.
    The setting is on the "Creative AudioHQ" at the "Surround Mixer" selection. It is called "Digital Output Only". Or if you use the little icon on the taskbar, at the "Speakers" on "Speaker Selection" you have the same option (a check mark under the selection of speakers).
    2. If you read the FAQ, you will get surround sound (5.) ONLY from DVD-Video that are encoded in DolbyDigital or DTS and ONLY if you pass-trough the digital signal to the receiver to do the decoding. In ALL other cases you will get STEREO PCM signal.
    3. If your receiver is a decent one you should have an analog surround input (5. analog input). in that one you can plug the analog outputs from your card in order to have surround sound all the time (like in the games).
    Message Edited by SoNic2367 on <SPAN class=date_text>09-25-2006 <SPAN class=time_text>06:24 AM
    Message Edited by SoNic2367 on 09-25-2006 06:26 AM

  • How do I calculate 'uptime' of a digital output

    Hi everybody,
    I'm new to these forums and I am currently evaluating Labview for a series of lab tests where we measure energy balance in a chemical reaction. I've already 
    I have a USB 6008 wired to a relay drive (thanks to these forums) and a heating element and I want to measure the total time heating element is 'on' during 24 hours to calculate the energy the system is getting. The heating element switches on and off based on the signal of a thermocouple.  Is there an easy way to measure the seconds that the output port wire to the heating element is active? Device-independent would be preferable (like measuring the signal uptime of the input of the digital output of the USB6008)
    I tried a lot of options today, like while loops, sequences, case structures following several postings here but all of them failed miserably - while the problem sounds so easy. I could easily do it in the hardware by wiring the output of the relay drive to a bauser timer, but that would be giving up too soon
    Any help would be appreciated.
    Best regards,
    Dimitri

    Hi Dimitri,
    Welcome to the NI Forums! It's good to hear that you've already received some help here.
    Q: Is there an easy way to measure the seconds that the output port wire to the heating element is active? 
    A: Yes! The method we can use to perform this action depends on the sort of architecture that you're using at the moment, however we can take advantage of the section of your code which defines whether the line should be on or off. When it's on, using a While Loop we can  use a Timestamp to keep track of the current System clock; this Timestamp will update on every loop iteration. If we use a reference Timestamp which is created outside of the While Loop when we first begin to drive the line high, we can simply work out the difference between the current Timestamp and the reference Timestamp to get the total time.
    This kind of code will also be device independant because it relies only on the computer it is used on.
    I hope this helps!
    Alex Thomas, University of Manchester School of EEE LabVIEW Ambassador (CLAD)

  • How do I keep a digital output from SCC DO01 from fluctuating states?

    Background: Hooking an ohm-meter across a digital output from a SCC DO01 isolated optical switch shows that the resistance fluctuates and at times goes open circuit. It appears directly related to the LabView code where I'm writing to this digital line within a WHILE loop. The loop has a variety of other operations going on. These other operations, I believe, are causing this problem due to timing or something.
    How can I improve the reliability of this digital output? There must be some method of establishing priority within a WHILE loop.
    Really appreciate the help.
    Hunter

    Howdy, Justin
    Thanks for your reply.
    I've actually been connecting the meter across Vss and Vout. Actuating the digital output, I can see the state of the switch. Attached is the VI which involves this DO01, specifically, it's associated with the VFD RUN/STOP.
    Since I sent this question out, I've actually gotten some help from Andy Watchorn of NI. This switch holds state much better.
    All the best,
    Hunter
    Attachments:
    VFD_ControlVIs.zip ‏120 KB

  • How to generate multiple digital outputs (square waves delayed) at 50 kHz?

    I would like to generate 3 digital outputs like the picture attached at 50 kHz. Using the "digital pattern generator (marching values).vi", I can generate 3 digital square wave but without the delay time. How can I do that?
    I'm using the card PCI 6034E.
    Thank you
    Attachments:
    digital outputs delayed.png ‏8 KB

    Hi,
    the digital pattern generator (marching values) only shifts the binary value of the first signal and sample to the next signal/sample.
    Have you tried generating your waveforms via build waveform and use t0 terminal to change the lead delay?
    In general, this DAQmx example could be helpful which you can modify to your needs.
    DAQmx Write Digital Channel- External Clock: https://decibel.ni.com/content/docs/DOC-11142
    Regards,
    Thomas