In a code for a a test rig ( LV7.1 + Win XP ) I am scanning all digital
inputs once every 50ms inside a timed loop. But there is one input from
a proximity switch that I need to be able to respond to immediatley as
it changes state.
 Any delay  of even a few ms, will add on to the reversal error of a servo drive motor.
 Ideally what I am looking for is a kind off  Interrupt
or  Event Structure for an external field input.  I know this
is not there in LV, but would be ineterested in achieving the same
functionality by some other means.
Thanks
Raghunathan
Raghunathan
LV2012 to Automate Hydraulic Test rigs.

Hello Raghunathan,
It LabVIEW if you are polling your device every 50ms for data, you will only get updates from your device every 50ms. It sounds like you are looking for some sort of change notification or change detection from your board. It is likely that you will get a much better and faster response to this question on the Multifunction DAQ or Digital I/O discussion forums since this is primarily a hardware question. If you decide to post to the hardware discussion boards, it may also be a good idea to list the specific hardware you are using so that people with similar setups can share their experience.
Best of luck,
Chris J
Multifunction DAQ board
http://forums.ni.com/ni/board?board.id=250
Digital I/O board
http://forums.ni.com/ni/board?board.id=70

Similar Messages

  • Triggering an event with a digital input

    Hello all,
    I'm writing my first Labview program.  I used an architecture I found on the forums here, and it has been very helpful in getting me started.  This architecture uses two while loops, one containing an event structure and one containing a case structure.  (This is a queued state machine architecture, I believe).
    Part way through the programming, we decided we needed a sensor to make sure the part was in the test fixture during the test.  If the part is removed during the test, we'd like to safely stop the test.  So basically, I need to monitor a digital input (on an NI-USB-6525 module) and enter the "Stop" case if the digital input turns off.  I would also like to make sure this digital input is on before entering the "Start" case.  I don't care if the input changes state when the test is not running, nor do I care about its state during the "Exit" case.
    I'm really not sure how to add this functionality to my "stop" case.  I don't even know if it's possible.  I've been researching DAQmx events, but I haven't found an example or answer that aligns with my particular problem. 
    I've attached my code.  It's incomplete right now - I still have a large number of steps to add.  I wanted to get this issue figured out before I programmed any more steps.  A preview of the code showing the basic architecture is shown in the picture below.
    Does anyone have any ideas or suggestions for me, or questions if my problem is unclear?  Also, if you see anything else in my code that will be problematic, please let me know.
    Thanks in advance!
    Attachments:
    Main_Loop_072412.vi ‏195 KB

    I should also add that I looked into event dynamic registration, but it seemed incompatible with my issue.  I don't want my top loop to run only when an event triggers it - I want it to run all the time so that it can immediately respond to button presses. Also, most of the triggering I found was based on value change.  I care about the actual value, not just that it changed.
    I don't want to do anything that will bog the code down too much since it is important that the system respond immediately to inputs, especially to the stop or exit button presses.
    I'm sure I am missing something very basic here.  I'm used to ladder logic, where everything is simple and straightforward. 

  • Joe Meek Twin Q Pre-Amp and Elite Pro SPDIF/Digital input probs

    Hi. I'm wondering if anyone can help. I've just purchased a Joe Meek Twin Q Pre-Amp and I specifically bought it for a new Rode mic I've just got and it needed phantom power. I also paid a little extra for the digital 'outs', thinking I could take an optic or SPDIF out into the Elite Pro breakout box. The problem is, is that digital is not recognised at all - in Audio Codes it states it's an invalid signal. However, SPDIF is recognised saying it's a stereo signal at 48,000hz, but is only being 'heard' in my right channel.
    I have tried the line out into Line In 3, and there's no problem there. Joe Meek representative said it should be working as long as the bit match is the same in both units, which as far as I know is. Am I missing something here? I'm awaiting Creative to get back as it seems to me to be a breakout-box hardware problem, but I could be missing something?
    Does anyone have any experience and/or advice/info?
    Thanks in advance

    Well, since you're not getting response, let me see what I can do.
    I think you're saying the optical connection isn't working, but the coax (SPDIF) one is working, and then you're only getting the mic signal on one channel. The second part is easy to explain, but I never remember the solution suggestions. TOSLink/SPDIF, essentially, are stereo signals, and your preamp is simply putting its channel 1 signal on one side and its channel 2 signal on the other. If you had a second mic connected to the other connector, you'd have one mic on the left channel and the other on the right channel. Basically, you need to treat it as a mono signal and then either pan it into the stereo field, or just duplicate (convert) it to stereo. I'm sure there are ways, but someone else needs to join in with some experience. I'm not sure, but it seems to me if, say, you've put the mic in the channel 1 connector, you could take the channel 1 (analog) output and patch it into the channel 2 line input, and your digital outputs would probably get you the mic signal on both sides.
    On both devices, the TOSLink/SPDIF signals are, to the best of my understanding, basically the same thing in two forms. If one is working, than the other should be working too. That suggests to me either hardware brokenness in the preamp's optical out, or the Elite Pro's optical in. or a problem with the optical cable. CL's optical outs can be checked to see if they are putting out red light: if they aren't, there's a problem. That probably applies to the preamp, in this case. You can simply connect the Elite Pro's optical output to its optical input and record something from the digital input device. If that works, the cable and the digital input are probably OK, and it most likely the preamp's digital output is broken (although it could be a strange compatibility issue). If it fails, then it's most likely either a bad cable, or the Elite Pro's optical input is broken. Trying another cable, or some other piece of gear you have that outputs optical, ought to sort out which it is.
    -Dave
    [email protected]

  • How can an unconnected indicator read an FP digital input?

    SYSTEM DESCRIPTION:
    A Dell desk top computer with a Field Point system attached. There are a variety of modules including analog input, 2 digital inputs, relay out, Strain gage input, quadrature input. The system is running XP. The Labview program is written in v6.1.
    PROBLEM
    In an application written by others, I have found 4 front panel indicators that react to Field Point digital inputs. On the block diagram, the indicators are not wired to anything. They have no local variables and no global variables associated with them. How can they be reacting to the FP inputs? The problem is that one of the indicators reacts to the wrong input and I need to fix it.  See "In(Rescue)Limit, In(Cargo)Limit, 4067 Out Limit and EStop".
    Also, when the vi is launched, it starts up the FP system and the vi has no FP vi's in it and none of the sub-vi's have any FP vi's in them either. Any clues how this could be working?
    I have attached the vi. There are other vi's in this project, just too many to include unless more information is needed.
    Thanks,
    Chris Dreike
    Advantage Automation, Inc.
    [email protected]
    310-214-2175

    Chris,
    It doesn't look like you attached the VIs.
    You can use front panel DataSocket binding to link an indicator or control to a FieldPoint ethernet item. Right-click on the indicator and choose Data Operations>>DataSocket Connection.
    Regards,
    Aaron

  • Error while adding a custom field with Input help via AET

    Hi All,
    I need to add two custom field under Service orders at Item level in component BT140I_SRVP.
    One field is required to have the input search help f4 and autopopulates the second field
    I am able to add one field(not requiring help) successfully through AET .
    I have created one Zsearch_help in se11 and its successfully running  and Autopopulating seocnd field while I am testing it
    While adding second field through AET,I need to enter following details as -
    field label,search relevant ,serach help etc.
    When I type the name of my 'Zsearch_help' against field search help it gives me following error
    'Search help is not compatible'.
    Secondly,not getting getter and setter methods for the attrributes in BTAdminI.
    Last,please tell me if i create zhelp and activate it,would it automatically appear in the list on AETwhile assiging it to input field?
    Please help me out.Kindly be detailed as I am new to SAP CRM.
    Thanks,
    Shivani

    The question is answered in CRM 7.0 forum:
    Getting error while adding a custom field (with input help) through AET

  • Usb 6009 digital input

    Dear All!!
    With the following vi. I'm trying to receive a 5V signal in a digital input, using a usb-6009 device.
    I would like to use the 5 VCC supply, available in pin 31 of the same device and send it to pin 17, representing line0 of port0. During execution, 'm physically connecting and disconnecting  these pins in order to see the difference in a led indicator. Unfortunatelly, the led is always on, even if both pins are disconnected.
    Could somebody help me? I would be very pleased.
    Thank you very much in advance,
    Miren
    Attachments:
    proof.vi ‏38 KB

    Hi Miren,
    "the led is always on, even if both pins are disconnected"
    RTFM?!
    They use open collector inputs with an internal pullup resistor of 4.7k, so you actively have to pull down the input to GND to see a difference...
    Best regards,
    GerdW
    CLAD, using 2009SP1 + LV2011SP1 + LV2014SP1 on WinXP+Win7+cRIO
    Kudos are welcome

  • How to acquire serial data on a digital input line with good performance?

    Hello,
    we have a performance problem with our realtime controller. Our objective is, to read a 24-bit long digital waveform from a digital input line. To do this, we supply a clock signal (236 KHz)  to the PFI1 Line of our DAQ Board. On each rising edge of the clock, a new bit is set on the digital input DI0.
    Our hardware which transmits the data, is triggered through a digital output from our realtime controller. On each edge on this output, the hardware starts a serial transmission of 24-Bits.
    Everything works fine except the bad performance of our realtime controller. We want to acquire the 24-Bits in a 1ms timed loop. To measure performance we wrote a test program. In that, we only triggered the hardware and transfered the data to the realtime controller. The task which is doing this job, has a approx. CPU-Load of 30%, which is, in my humble opinion, very high. The task is not waiting for data or anything else! We have earlier implemented a control which is also using a 1ms timed loop. This control is sampling 2 analog input signals, 2 counters. Futhermore it's sending telegrams with CAN and doing many calculations. The strange thing is, this much huger program has a CPU-Load of 25%. Does anybody know where the problem is?
    For the better understandig I attached our test-program to this text.
    We're using:
    PXI-8175 realtime controler
    PXI-6221 Multifunction DAQ
    Thanks!
    Regards, 
       Crest!
    Attachments:
    dig_test.zip ‏51 KB

    Hello,
    First of all 30% CPU-Load is normal because the DAQmx-driver needs a lot of resources.
    In your programm you should place a wait (for example with 1ms) into the while-loop which causes
    lower CPU-Load.
    If this is not enough you should build your vi like in the following example.
    Regards,
    Christian
    Attachments:
    Read Dig Port.vi ‏51 KB

  • How can i connect 24VDC to digital input (usb 6008)

    hello,
    how can i connect 24VDC to digital input (usb 6008), is it possible with some optocoupler?
    thanks

    The 6008 is a static DIO, so speed shouldn't be an issue.  Therefore an optocoupler should work.  Just make sure you get one the meets your specs.
    There are only two ways to tell somebody thanks: Kudos and Marked Solutions
    Unofficial Forum Rules and Guidelines

  • Audigy 4 Pro digital input 16 - 24

    I have a Sony MDS-JB920 minidisc deck hooked up to my Audigy 4 Pro through the external box. Works fine.
    However, the Minidisc deck allows one to set both the digital input and output to either 6, 20 or 24 bit. As the Audigy 4 Pro is 24 bit, I've set the deck to 24 bit for both in and out. So far no problems. If I watch the settings panel whilst playing a minidisc however, it indicates that the signal coming from the MD deck is 6 bit, although the deck is set to supply 24 bit through the SPDIF out.
    When I put the MD deck on rec mode whilst the PC is supplying audio feed, the MD deck loops it back to the SPDIF input of the Audigy and then the software does display 24 bit signal coming from the MD deck.
    This is very confusing to me, does anyone have an explanation?

    CMSS is an effect used for stereo sounds, to emulate surround sound for them. It has no effect on the DVDs you're playing as you're just outputting the AC3 signal so the speakers can decode it.
    If you're using a digital connection, then CMSS will not have any effect for other sound either, you need to connect through multiple analog connections to get that sound. A standard digital connection (coaxial and optical SPDIF) can only pass over either a stereo PCM signal, or an encoded AC3 stream (like on your DVDs). Normal sound like music or games will only be passed over as stereo PCM, so there is no CMSS effect there.
    If you can connect your amplifier through several analog connections, then you can use CMSS aswell, otherwise your amplifier might have it's own upmix option like ProLogic.
    Cat

  • How to I connect Sourcing digital output from My Interface Board to NI USB 6501 channel configured as Digital input

    When I connect an input to DI channel of USB 6501 card  from my board which has sourcing Output t, iIn the Off state it is not pulled down properly. The volatge on the port in is 2.1V -2.5V based on the pull down resistor on my board. I suspect that  it acts as a voltage divider.
    The state on the card is still show as "HIGH "state, even my sourcing output driver has a pull down  resister.  when I use this interface board for PCI mseries devices it works fine. Do the pull down resister on my sourcing output is not worth. Is this because of pull up resister 4.7k inside USB card 6501.
    USB 6501 specifications shows the Digital input accepts both source and sink modes. By default the card is in sourcing digital input mode. How do we can convert this in Sinkind digital input mode.
    Could anyone Please give your suggestions to overcome this issue .
    Thanks you.

    You really should not have both a pull up and pull down on the same line.  Really weird things can happen.  If you insist on having a pull down on your board, then I highly recommend putting a digital buffer chip between the DAQ and your board.
    Some boards with DIO have a pull up, while others have pull down.  You just have to watch the specs.
    There are only two ways to tell somebody thanks: Kudos and Marked Solutions
    Unofficial Forum Rules and Guidelines

  • I was given an assingment, but have no idea where to begin. The assingment is to create a text file using notepad with all of my digital inputs and some how make those imputs show up on my digital indicators on my control pannel

    I was given an assingment, but have no idea where to begin. The assingment is to create a text file using notepad with all of my digital inputs and some how make those imputs show up on my digital indicators on my control pannel.
    When it was explained to me it didn't sound to hard of a task, I have no LabVIEW experience and the tutortial sucks.

    StevenD: FYI, I did NOT give you the one star rating. I would never do that!
    StevenD wrote:
    Ow. Someone is grumpy today.
    Well, this is an assignment, so it is probably homework.
    Why else would anyone give HIM such an assigment, after all he has no LabVIEW experience and the tutorials are too hard for him?
    This would make no sense unless all of it was just covered in class!
    This is not a free homework service with instant gratification.
    OK! Let's do it step by step. I assume you already have a VI with the digital indicators.
    "...but have no idea where to begin".
    open notepad.
    decide on a format, possibly one line per indicator.
    type the document.
    close notepad.
    open LabVIEW.
    Open the existing VI with all the indicators.
    (are you still following?)
    look at the diagram.
    Who made the program?
    Does the code make sense so far?
    Is it a statemachine or just a bunch of crisscrossed wires?
    Where do you want to add the file read?
    How should the file be read (after pressing a read button, at the start of the program ,etc.)
    See how far you get!
    Message Edited by altenbach on 06-24-2008 11:23 AM
    LabVIEW Champion . Do more with less code and in less time .

  • Digital Input Cannot Display this Video Mode Optimum Resolution 1280 x 1024 60hz.

    HP Pavilion h8-1360t, Windows7 home premium 64-bit,  AMD Radeon HD 7570 graphics card.
    error message: Digital Input Cannot Display this Video Mode Optimum Resolution 1280 x 1024 60hz. 
    I get the error message as soon as Windows opens and the desktop displays.  Then it goes black with that message.  I've been using the computer for awhile and I had it so that when I maximized a window it would go across both screens.  I have two monitors on the graphics card.  Somehow I changed the settings so that a program would maximize to one monitor or the other.   That is how I want it to work.  Maybe I activated HydraVision.  Now I have the problem when I start.
    Also now when I boot to Safe Mode I get the message that there is no AMD graphics driver installed, or it is not functioning properly.  I have tried to update it and the computer tells me I have the most recent version installed.   I would like to uninstall it and reinstall it, but I'm a little worried I won't get it installed and be without video.  Something like that happened to me once before years ago.
    Could someone tell me what I should do please?
    Thanks,
    Jim Allen

    HP support is here:
    http://www8.hp.com/us/en/contact-hp/contact.html
    In safe mode you should uninstall the driver, then try to boot normal again.
    Then check if driver was installed by win7.
    If not go go AMD website and download latest driver for your card.
    V.
    *** Say 'Thanks' with Kudos ***

  • Monitors with Digital Inputs

    What monitors are available that accept the Toslink input directly? Do the keyboard and on-screen volume controls still work with this arrangement?

    I believe Tannoy make a set of the Elipse range of speaker with digital inputs as well. I have no idea why you would want to do this though. I suspect the gains in quality would be tiny if anything at all. You'd be better to spend more money on something less techy and get something that really sounds great!

  • How can I use 4 DIO lines as digital input in a E series-SC 2050-ER8 set up ?

    I have a DAQ system with an E series DAQ card that is connected to SC-2050 and ER8. I want to use 4 DIO lines (out of 8) for digital input. How can I do this?

    Hello Suresh,
    There are a variety of ways to accomplish this. If you are using LabVIEW, you will use the DIO Port Config VI and the DIO Port Read VI. You will use the line direction map input of the DIO Port Config VI to setup which 4 lines you want to be the input lines. The LabVIEW shipping example entitled 'Dig Multi-line Direction (E) VI' shows how to use the lines of the digital port on an E-Series device for input and output.
    If you are using NI-DAQ function calls, you can use the Dig_Line_Config and Dig_In_Line calls to configure a digital line for input and then read from that line.
    I hope this helps.
    Regards,
    Todd D.
    NI Applications Engineer

  • Can't change sample rate for digital input on Mac Pro

    Hello all,
    on my Mac Pro with 10.4.10 I can't change the sample rate for the digital input. Whenever I choose 48000 or 96000 Hz it returns to 44100 Hz after a few seconds. Feeding a 24 bit/96000 Hz signal from an external ADC into the optical input doesn't help. No input signal is available for digital recording software such as Sound Studio or Cubase. After changing the sample rate in audio midi configuration to 96000 Hz the sound can be heard for a few seconds but when the setup returns to 44100 automatically the signal is, of course, lost.
    I've deleted all relevant preferences and restarted with resetting paramter RAM. Still the same. With external hardware such as M-Audio Firewire equipment setting the sample rates works properly.
    Thanks to all for helpful clues.

    Hi,
    when E&M signaling is configured on digital interface like the VWIC is, 2 or 4 wires operation is not applicable because there are no wires at all, and reported only for compatibility with the analog E&M card.
    Consequently, you cannot configure that and it will not make any difference to effect of the connection.
    Please rate post if it helps!