I am reading i/o tags from an allen bradley 5/05 through rslinx using ethernet settings. Everything works fine, I read and write to the tags all day. However, If I go online through the ethernet it seems like all the bandwidth is used up and labview displays an error. maybe opc times-out. When labview is retrieving just i/o through opc, it works fine. But if it is retrieving i/o and gathering analog data from a MIO card and you try to get on the plc it faults out. Anything would help. I have attached i/o read/write vi
Attachments:
NEW_OPC_Digital_Functions.vi ‏134 KB

You could try accessing the i/o on the plc using the 'Server Explorer' program. If you do not have that program you can download it at: :Server Explorer. Server Explorer is a utility that allows you to view and interact with available OPC servers. You might also try accessing the PLC from two different computers at the same time to see if it is a problem on the PLC side. There are not any known issues with DataSocket OPC like this so you might also contact Allen Bradley about the issue.
Regards,
JR A.
Application Engineer
National Instruments

Similar Messages

  • Response time between LabVIEW w/DSC module and RSLinx OPC server hosting FlexLogix PLC tags too long

    We are experiencing communication response time delays between LabVIEW with DSC module and RsLinx OPC Server hosting all FlexLogix PLC tags (around 500-600 tags).
    The nominal response time for the system watchdog is < 500ms, but we occasionally have spikes of up to 1.5 seconds once every few days even when the system is idling.
    Changing more than six PLC connected shared variables at the same time from LabVIEW also causes the watchdog response times to spike above 500ms.
    Our watchdog is programmed so that LabVIEW toggles the watchdog bit to 1 as soon the shared variable event detects that the PLC has toggled it to 0. The PLC, however, waits 300 ms until it toggles it.
    Our system:
    Windows XP SP3
    LabVIEW 9 F3
    RSLinx Opc Server v2.54
    Allen Bradley FlexLogix PLC

    What is your update rate set for in the RSLink OPC server?
    You aren't toggling the same flag from both ends are you?
    Ben
    Ben Rayner
    I am currently active on.. MainStream Preppers
    Rayner's Ridge is under construction

  • Connecting between labVIEW and PLC S7-1200 using EPICS

    Hello everyone,
    I'm trying to connect between LabVIEW and PLC S7-1200 using EPICS. I did it using OPC and it succeeded and the communication was done, so right now i'm trying to do it using EPICS. so Can anyone help me with that?
    Thanks in advance.
    Ahmed

    Hello,Ahmed:
    Now I'm trying to conect S7-1200 to Labview by OPC server 2012, I'm newer for both PLC S7-1200 and OPC server. by the help file of NI's OPC I tested many times, but lost totally.
    You mentioned that you have succeeded making the connection between them, could you please help me :
    1) How to set in Simense TIA software? I can set the PLC's IP address now, that's all;
    2) OPC server setting.
    if there is a video, that will be great.
    thanks a lot.
    Delphi77.

  • Which protocol is recommende​d to communicat​e between LabVIEW an the S7-300 PLC?

    Hello,
    I'd like to communicate between LabVIEW (CompactRIO) and the S7-300 PLC.
    Which is the protocol NI recommend to use?
    I read, that TCP/IP over OPC and profibus work fine. Maybe MPI or Modbus, too.
    But I would favor a cheaper solution like the communication directly over TCP/IP. The problem is in my opinion, that Siemens modified the TCP/IP protocol and the protocol itself is not public. I found an example library at ni.com but this was build by using reverse engineering. And I'm not sure, if such a library would work reliable.
    I know this topic is interesting for many people, but I could not find a general recommendation here in the forums.
    Regards

    I have direct experience using the NI OPC servers to talk to Siemens S7-300 PLCs, and it's by far the easiest way I've found to communicate.  There may be 'less expensive' options out of the box, but from purely a development standpoint, it's very fast and easy to get working.

  • Communicat​ing between LabVIEW and Basic Stamp 2.0

    Hello,
    We are trying to control the movement of a Parallax Boe-Bot (robot with
    Board of Education) via LabView programming.  The BOE operates on
    Basic Stamp programming to control the pulse width sent to two servo
    motors.
    Is there a way to establish communication between LabVIEW and Basic
    Stamp 2.0?   We need to send commands from LabVIEW to the
    Basic Stamp to control the pulse width and therefore the rotation of
    the two servo motors.  We also need to send a signal from an
    accelerometer based on the robot to the LabVIEW ADC. 
    The ultimate goal is to do this with wireless communication, but for
    right now we are simply trying to figure out any way to send the data
    between LabVIEW and the Basic Stamp.
    Any ideas?
    Thank you,
    Adam

    Hi Adam,
    You can communicate with a BASIC Stamp microcontroller over GPIB using VISA.  To see some LabVIEW example code, just search for GPIB in the NI Example Finder (Help>>Find Examples). This will show you the basics of GPIB communication in LabVIEW.  I also found this link by searching the NI discussion forums for "basic stamp"
    http://www.parallax.com/html_pages/downloads/softw​are/software_basic_stamp.asp
    Here you can download an example using LabVIEW 7.0 or higher to communicate with a BASIC Stamp 2.
    I hope this is helpful!  Let us know if you have further questions.
    Megan B.
    National Instruments

  • Reference Library for Converting Between LabVIEW and XML Data (GXML)

    Please provide feedback, comments and questions on the Reference Library for Converting Between LabVIEW and XML Data (GXML) in this thread.
    The latest version of the NI GXML Library is availble in VIPM on the NI LabVIEW  Tools Network repository.

    Francesco, Thank you for the feedback.  With this component it was my intention to make a more "terse" version of the LabVIEW Flatten to XML VI that was also supported on RT and that gave the user more flexbility regarding the structure of the parsing type definition. I think you are right that the XML parser is not compliant to section 2.11 of the XML spec.  The parser does specifically looking for a #D#A and this appears to be an oversight on my part.  Please confirm for me, the specifcation is saying that the XML parser should be able to recognize three possibilities as an "end of line" character: #D#A, #D, or #A.  Am I reading this right?There are more efficient (and in some cases much more efficient) ways of sharing data between LabVIEW and LabVIEW: some examples are flattened binary strings and the datalog binary format.  XML is slower than these optons but the upside is that it is human readable.  Furthermore XML is inherently hierarchical which is convenient for complex data structures like clusters of arrays of clusters, etc.  If you don't care about human readability then you are correct XML doesn't make as much sense.I will return to the GXML source code and try to fix this in the near future but I would hope that instead of creating yet another custom VI from scratch that you could reuse what I have provided for you.  I included enough documentation in the source code so that users could make some modificiations themselves. The target application for this reference library was LabVIEW to LabVIEW communication.  As such I documented the schema on the dev zone document from a LabVIEW perspective.  It includes all the supported datatypes and all the supported data structures (cluters, arrays, multidimensional arrays, clusters of multidimensional arrays, etc.)  I do see some value in making a more conventional XML spec but the time investment required didn't really line up with my intended use case. Were there any other downsides to GXML that I have missed?  Best Regards, Jeff TippsSystems Engineer - Sound and VibrationMessage Edited by Jeff T. on 04-21-2010 10:09 AM

  • Best communication method between LV Application

    Hello Together,
    I'm looking for the best communication way between two LabVIEW Applications. As VI is clear, I can use a Queue or a global variable and so on.
    But what is the best, when I compile the VIs later to DLLs or Applications. Till now we always use TCP/IP, but I think there must be a better way instead of this.
    So if anybody has an idea - it's very welcome.
    Thanks in advance
    Markus
    Solved!
    Go to Solution.

    Traxx wrote:
    What I don't like with TCP/IP that you always need a second thread (while loop) who handle the TCP/IP communication. I thought that there must be an easier way.
    I also thought that shared variables are always limited to one application. Thanks for the ideas...
    That second loop is a loop that YOU control. If you go with shared variables you are a slave to whatever they can or can not do. Besides, they run on top of TCP/IP so it is not out of the picture.
    Its your call,
    Ben
    Ben Rayner
    I am currently active on.. MainStream Preppers
    Rayner's Ridge is under construction

  • How to Communicate a string between LabView 7.0 and VB using TCP/IP

    HI
    I want to know how to communicate , " by passing a string  "  between LabView 7.1  and VB 6.0  using tcp/ip . Please if anyone couild help me on this..
    Regards
    Ashish Doshi

    Ashish,
    I've got great news for you! LabVIEW has built in TCP functions. They are located in Data Communication>>Protocols>>TCP. From the LabVIEW side, I think you'll find everything you need in there. Good luck!
    Chris C
    Chris Cilino
    National Instruments
    LabVIEW Product Marketing Manager
    Certified LabVIEW Architect

  • Communication problem between NetBeans and Tomcat

    hi!
    i got a quite mysterious problem. here is what happens:
    - i start NetBeans 5.5.1 (the first time)
    - i want to debug my JSF-Project, the Debugger starts
    - After a few seconds the debugger waits for tomcat (it sais: "Waiting for Tomcat...") and tomcat starts
    - Again after a few seconds the tomcat-debugger-output sais "Tomcat startet in 3333 ms".
    okay.
    when i enter http://localhost:8084/ in my browser i get the tomcat homepage, so the server has definitely started! But nothing happens in NetBeans and nothing happens with my project....
    In the lower-right corner i see this blue working-bar that sais "deploying project" but nothing happens. The Project-Debugger-Output still sais "Waiting for Tomcat..." but nothing happens...
    And after something around 3 minutes (i guess it's a timeout) i get the error "Starting of Tomcat failed." But is HAS started, i can login to the Administration-Area in my browser!
    so i guess there is a communication problem between netbeans an tomcat. Netbeans waits for a message from tomcat but tomcat doesn't send it..or netbeans doesn't understand it.
    But the story goes on:
    When i press the debug-button a second time it takes only a few seconds till i get the message: "Tomcat server port 8084 already in use". OF COURSE! Because Tomcat has already startet and can't be stoped by NetBeans.
    i'm trying to solve this problem for 4 days now, so i would be very happy if anyone has an idea where to start/continue the search...
    thanks,
    flo.
    some system-info:
    - windows vista business 32-bit
    - no firewall is running
    - AntiVir Personal Edition IS running
    - Yahoo Widgets Engine IS running
    - no other software is running
    and finally the tomcat-log:
    Using CATALINA_BASE: C:\Users\Administrator\.netbeans\5.5.1\apache-tomcat-5.5.17_base
    Using CATALINA_HOME: C:\Program Files\NetBeans\enterprise3\apache-tomcat-5.5.17
    Using CATALINA_TMPDIR: C:\Users\Administrator\.netbeans\5.5.1\apache-tomcat-5.5.17_base\temp
    Using JRE_HOME: C:\Program Files\Java\jdk1.5.0_12
    Listening for transport dt_shmem at address: tomcat_shared_memory_id
    21.09.2007 18:27:50 org.apache.catalina.core.AprLifecycleListener lifecycleEvent
    INFO: The Apache Tomcat Native library which allows optimal performance in production environments was not found on the java.library.path: C:\Program Files\Java\jdk1.5.0_12\bin;.;C:\Windows\system32;C:\Windows;C:\Windows\system32;C:\Windows;C:\Windows\System32\Wbem;C:\Program Files\QuickTime\QTSystem\;C:\Program Files\ThinkPad\ConnectUtilities;C:\Program Files\Common Files\Teleca Shared;C:\Program Files\Common Files\Adobe\AGL;C:\Program Files\MySQL\MySQL Server 5.0\bin;C:\Program Files\cvsnt;
    21.09.2007 18:27:50 org.apache.coyote.http11.Http11BaseProtocol init
    INFO: Initializing Coyote HTTP/1.1 on http-8084
    21.09.2007 18:27:50 org.apache.catalina.startup.Catalina load
    INFO: Initialization processed in 1862 ms
    21.09.2007 18:27:50 org.apache.catalina.core.StandardService start
    INFO: Starting service Catalina
    21.09.2007 18:27:50 org.apache.catalina.core.StandardEngine start
    INFO: Starting Servlet Engine: Apache Tomcat/5.5.17
    21.09.2007 18:27:50 org.apache.catalina.core.StandardHost start
    INFO: XML validation disabled
    21.09.2007 18:27:53 org.apache.coyote.http11.Http11BaseProtocol start
    INFO: Starting Coyote HTTP/1.1 on http-8084
    21.09.2007 18:27:54 org.apache.jk.common.ChannelSocket init
    INFO: JK: ajp13 listening on /0.0.0.0:8009
    21.09.2007 18:27:54 org.apache.jk.server.JkMain start
    INFO: Jk running ID=0 time=0/31 config=null
    21.09.2007 18:27:54 org.apache.catalina.storeconfig.StoreLoader load
    INFO: Find registry server-registry.xml at classpath resource
    21.09.2007 18:27:54 org.apache.catalina.startup.Catalina start
    INFO: Server startup in 3626 ms

    As i wrote before, the same problem occured for me. I have found a solution which is : Go to tools menu and then select options . In the proxy info, select No Proxy.
    I hope this help you

  • I am having one application which i am going to install on my ipad and i am having one external device having USB interface. I want to have communication in between  my device and ipad over USB/BT. is it possible

    My external device is having male USB connector. The cable available in market are having can be plugged to the device having female connector.I will need converter in between as my device is having male connector. Can i get such cable? If yes can i establish communication in between my app and device over these cables.I am not passing any audio/video data or photos.I am sending data frames. My device is having firmware and it sends data frames in firmware understandable format. Let me know can i have two way communication in between over USB/BT?
    Right now i am connecting my device with host PC and i want to replace my host PC with ipad.

    Thanks....
    will it be possible to establish communication in between my device and app. Because camera conection kit only transfers photos and videos and my device doesnt have any audio/video data.
    If yes, should i add photo header to my frames and will send as corrupted photo file or what needs to implement so that i can have sound communication in between.

  • Printer prints but display says Communication lost (device - control panel); Turn off then on.

    HP Color LaserJet CM3530fs
    The printer is printing when asked to do so by a computer but the display says:
    Error
    Communication lost (device <->  control panel); Turn off then on.
    The orange attention light is illuminated and the display is always lit and shows the statement above.
    It does not improve when switched off and on or power disconnected for long periods or pushing reset button at rear of unit.
    Embedded web server works normally and thinks that all is ok.
    Buttons on control panel do nothing.  eg. I cannot photocopy or scan.
    The printer is about 2 years old but gets very light use in a family home.
    Please help
    Thank you.
    Haig

    This seems to be a commercial product. For the best chance at finding a solution I would suggest posting in the forum for HP Business Support!
    You can find the Commercial Laserjet board here:
    http://h30499.www3.hp.com/t5/Printers-LaserJet/bd-p/bsc-413
    Best of Luck!
    You can say thanks by clicking the Kudos Star in my post. If my post resolves your problem, please mark it as Accepted Solution so others can benefit too.

  • I received a low ink warning on my mac for my epson artisan 837 printer. I replaced the cartridge that was low but it still reads low ink on the mac but reads full on the epson control panel. I am also receiving a communication error between the mac

    I received a low ink warning on my mac for my epson artisan 837 printer. I replaced the cartridge that was low but it still reads low ink on the mac but reads full on the epson control panel. I am also receiving a communication error between the mac

    What exactly is the error?
    And, we'd need some info re. your Mac model and OS version - you are not running iOS on it.
    You need to realize that this model has been discontinued and the last driver updates are dated about a year ago. If you are running Mavericks, there may not be an updated driver for it. But you can try to delete the printer and add it again to see if that will work.

  • How to convert labview data into opc tag

    Hi all,
    Can any one please tell me how i can convert the labview data global into a OPC tag? I have some data globals reading and writing data to the globals. Now i wanted to use a PLC device to send its outputs to the field.
    The PLC device will supports the OPC tags so i wanted t create OPC recognised tags in my labview. Is it possible. I saw that labview also having OPC functinalities. Please any one guide me in doing this.
    I will be very thankful to them
    Ramme..

    As I said, I believe you can do this for globals as well by opening its front panel (double click the global) and using a DS connection for the control that represents that specific global.
    As for other alternatives:
    NI sells the DSC module which comes with an OPC server and with better tags.
    You can use a common protocol like Modbus to interact with the PLC.
    You can use the custom protocol used by the PLC.
    The last two would require that you would change your program structure, so you would only want to use them under certain conditions.
    I believe the practical limit for OPC tags with DS is a few hundred tags, but I never used it myself so I didn't run into it. You can try searching the forums to find out more.
    Try to take over the world!

  • I have a communication error between Lightroom 5 and my printer. It prints photos about 1/2 strength in color. Printer checks out ok. WHAT CAN I DO?

    I have a communication error between Lightroom 5 and my printer. It prints photos about 1/2 strength in color.. The printer checks out ok. What can I do?

  • Can I increase communication speed between my Epson printer and the airport?

    I am having trouble printing large documents on my Epson printer.  typically I can print up to 10 pages of a document and then the printing fails.  In speaking with Epson, they are telling me it is the communication speed between the router (Airport Express) and the printer.  I am registering about 26 mbps and they are recommending 52 mbps.  It is connected through the wifi.  Signal strength is excellent.  The printer is in a second floor home office, and the Airport is located downstairs on the 1st floor about 15-20 feet away.  Is there a way to increase the communication speed without having to move the Airport upstairs (which of course would cause connection problems with other devices). Thank you

    Please check out the following AirPort User tip about base station placement for better bandwidth performance. The key is that a slight change in position of either the AirPort or the Epson printer may improve the situation.

Maybe you are looking for

  • Few questions about file sharing using airport

    I'm thinking about getting an AirPort Extreme, but I have a few questions: 1- I (must) use Ubuntu Linux at work and I would like to be able to acess my home files hosted at AirPort remotly. Is this possible? 2- Can I access my files on my iPhone usin

  • Automator bug?

    I am using Automator to copy several files to different locations, like this: 1. Get Specified Finder Items [one item – Item A] 2. Copy Finder Items [to Location 1] 3. Get Specified Finder Items [one item – Item B] 4. Copy Finder Items [to Location 2

  • What's all that code at the top??

    Hi. Just switched to Flash CS4 and things aren't quite the same. When I publish a file and look at the generated html file, there's a mile of code at the top of the page above the code which calls the swf. What is that?  I'm used to there being simpl

  • Error message on iPhone apps

    My wife's iTunes app on her Toshiba Qosmio keeps giving a series of error messages everytime she opens iTunes. It says something to the effect that the app in iTunes is newer than the one she is attempting to download. This is happening without the p

  • Capture Audio which can be heard from speakers..

    Hi.. I am currently facing a problem in capturing audio which can be heard from the speakers.. i.e. i want to capture audio generated by other applications. Till now I have been successful in capturing audio from microphone using JMF and Java Sound t